Vent Louvre Angle
#16487
Replies: 1 comment
|
This is almost certainly some combination of insufficient grid resolution to resolve the flow from the vent and/or the impact of the bulk flow field on the flow leaving the vent. Try this as an experiment. Make a simple input file of just your obst+louvered vent in the center of a volume with OPEN boundaries on all sides at a resolution that gives you mulitple grid cells (say 4 to 6) across the smallest dimension of your vent. |
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
I am experiencing a recurring issue with the vent louvre angle output.
I am attempting to configure the top fan to discharge at 45° in the negative X–Y direction within the horizontal plane, with an additional 15° downward inclination. Accordingly, I have specified the direction vector as (-0.683, -0.683, -0.2588).
However, the resulting airflow is directed almost entirely in the negative Y direction, which does not correspond to the specified vector.
I have encountered this issue on several occasions, leading me to suspect that the direction vector is not always being interpreted correctly.